Power Stations

(asked on 10th December 2014) - View Source

Question

To ask the Secretary of State for Energy and Climate Change, what estimate his Department has made of the dispatch period required to increase capacity at (a) nuclear, (b) combined cycle gas turbine, (c) open cycle gas turbine and (d) coal-fired power stations.


Answered by
Matt Hancock Portrait
Matt Hancock
This question was answered on 17th December 2014

A report by independent energy consultants Parsons Brinckerhoff commissioned by this Department considers the flexibility of coal and gas power technologies:

https://www.gov.uk/government/publications/technical-assessment-of-the-operation-of-coal-gas-fired-plants.

The table below contains information from the report and shows indicative start up times for coal, existing and modern gas combined cycle gas turbines (CCGT) and large and aero-derivative open cycle gas turbines (OCGT):

Technology

Notice to Synch* (mins)

Synch to Full Load (mins)

Hot Start

Coal

Existing Gas CCGT

Modern Gas CCGT

Gas Large OCGT

80-90

15

15

2-5

50-100

35-80

25

15-30

Warm Start

Coal

Existing Gas CCGT

Modern Gas CCGT

Gas Large OCGT

300

15

15

2-5

85

80

-

15-30

Cold Start

Coal

Existing Gas CCGT

Modern Gas CCGT

Gas Large OCGT

360-420

15

15

2-5

80-250

190-240

190

15-30

All Starts

Gas (Aero) OCGT

2-5

4-8

*‘Notice to Synch’ is the period of prior notice that a power plant requires to be able to start up the plant to the point of synchronisation.

The current nuclear fleet is not specifically designed for load following and generally plants will operate at their full nominal load. Plants that are offline for maintenance or refuelling will not usually be available to come back on line rapidly as there are a number of safety requirements that must be observed on re-start.